Author Topic: Admin Group Alarms Summary are different  (Read 2920 times)

Offline mszodiac

  • Sr. Member
  • ****
  • Posts: 232
  • Country: ca
  • Karma: +7/-0
    • View Profile
Admin Group Alarms Summary are different
« on: January 07, 2015, 03:36:09 PM »
How do I make the Admin Group Alarm Summary report the correct alarm status of all controllers? For example:

My admin group is : IPTel Group

I've got MCD1, MCD2, MCD3, MCD4, and MCD5.  They all have the same read only community string.  At the very top corner of MCD1, I see Group 'IPTel Group' Alarm Status: Major.  But when I click on MCD2, I see no alarms.  I've disabled/renabled Admin Group Management.


Offline johnp

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2202
  • Country: us
  • Karma: +66/-0
    • View Profile
Re: Admin Group Alarms Summary are different
« Reply #1 on: January 07, 2015, 03:47:55 PM »
I usually go to the snmp configuration and do a change and save when this happens

Offline mszodiac

  • Sr. Member
  • ****
  • Posts: 232
  • Country: ca
  • Karma: +7/-0
    • View Profile
Re: Admin Group Alarms Summary are different
« Reply #2 on: January 07, 2015, 11:10:39 PM »
Yes, I've done that too.  Same problem.

Offline 619Tech

  • Global Moderator
  • Sr. Member
  • *****
  • Posts: 230
  • Country: us
  • Karma: +1/-0
    • View Profile
Re: Admin Group Alarms Summary are different
« Reply #3 on: January 08, 2015, 06:39:11 PM »
Interesting, I didn't know of a way to shake this issue loose. I usually just wait (and wait) for it to resolve on it's own.

Offline mszodiac

  • Sr. Member
  • ****
  • Posts: 232
  • Country: ca
  • Karma: +7/-0
    • View Profile
Re: Admin Group Alarms Summary are different
« Reply #4 on: January 09, 2015, 10:42:34 AM »
I got this working by setting "Accept Requests From All Managers" to NO.  I entered all the IP addresses of all the elements belonging to the admin group, then resetting Admin Group management to disable/enable.


 

Sitemap 1 2 3 4 5 6 7 8 9 10