I have an MXe with two PSU and one is failing as I can see the alerts but it is intermittent so I need to be able to identify the failing unit from the maintenance logs, the entry is as below but I am not sure if the "1" indicates the first power supply or if that just means 1 of the 2 power supplies failed.
Warning 2021/Apr/22 17:00:07 REDUNDANT Power supply 1 removed
Right now both are working so the "SHOW STATUS REDUNDANT" does not help me identify the faulty one.
Any ideas?
Gerry
-
It definitely tells you which one, and they are labeled 1 and 2 (not 0 and 1 like some vendors would label this stuff). Replace PSU #1, it's probably just a bad fan, but as far as I know the fans in those things aren't field replaceable.
-
It definitely tells you which one, and they are labeled 1 and 2 (not 0 and 1 like some vendors would label this stuff). Replace PSU #1, it's probably just a bad fan, but as far as I know the fans in those things aren't field replaceable.
Thanks, I figured the 1 meant to identify which it was but was not sure if it would be 0 and 1 or 1 and 2. I have a replacement PSU to install tomorrow so I will find out for sure when I pull one out if the numbers match up.
-
You can also hot swap them so you don't need to shut down or anything.
-
You can also hot swap them so you don't need to shut down or anything.
Yes, I am aware of that and that will allow me to pull the first one and it should show as "Power supply 1 removed" in the logs.